The system shown below represents a typical DeltaV System. This comprises of Unspecified Safe AreaApparatus and I/O Modules and all other necessary apparatus such as power supplies, carriers, carrier extenders, etc. A system may be configured in a horizontal or vertical position depending on the type of carriers used. Each system has a maximum length of 6.5 meters (including interconnections) and may include up to 64 I/O modules.
General installation instructions of these components are covered in the DeltaVTM S‐Series and CHARMs Hardware Installation and Hardware Reference Manuals. Special installation requirements, applicable to the use in Zone2 hazardous location are covered here and are defined below. This system may also be placed in a Safe Area and have its field wiring enter a Zone2 hazardous area as long as all criteria listed below are met