CONTENTS:
-------
1. System requirements
2. Documentation
3. Program composition
4. Choosing the connection
5. Online RS232/485 Ecodrive/Diax
6. Online RS232 Indradrive
7. Online using SERCANS
8. Online via field bus
9. Simulation offline
10. Causes for noise in communication on RS232/485 Ecodrive/Diax
11. Malfunction in dialog "Motor parameters"
12. Field weakening operation of asynchronous motors with IndraDrive
13. Error at program start of DriveTop
14. Error at start of oscilloscope function
15. Crash when opening a file selector
16. Requried user rights (Windows 2000, XP with NTFS filesystem)
17. Supported firmware online
18. Online via field bus supported firmware
19. Supported firmware offline
20. Support address
*** 1. System requirements ***
- At least Intel 486 PC (Pentium 166 or higher recommended).
- Microsoft Windows 95, Microsoft Windows 98, Microsoft Windows NT 4.0,
Microsoft Windows 2000 or Microsoft Windows XP.
- At least 32 MByte memory.
- At least 60 MByte free space on fixed disk.
- To ensure a correct display, choose in
Display Properties->Settings->Font Size the setting "Small Fonts".
*** 2. Documentation ***
You can use the help function in DriveTop only when the documentation for
the used firmware is present on the system as well. If it is not, you can
assign other help systems with the menue item "Help->Settings". You can get
context sensitive help any time via the right mouse button, as long as the
help system is installed.
*** 3. Programm composition ***
When you start DriveTop, various programs are started (DriveServer, SCP,
SCP DDE Server, OfflineServer), depending on the chosen communication type.
*** 4. Choosing the connection ***
With drives of the Indradrive, Ecodrive and DIAX ranges, you can communicate
online via the RS-232 interface or via a SERCANS card. Offline, you can compose
the desired configuration of your equipment (Ecodrive and Diax), and afterwards,
you can create parameter files, to load them online into a drive later.
Communication via SoftSERCANS is available when SoftSERCANS was installed on the
computer in Version 2.
If a Hilscher Profibus master was installed in the system, DriveTop can use the
Profibus for parameter communication if a Hilscher CIF-Device driver was
configured.
*** 5. Online RS-232/485 EcoDrive/Diax ***
You should use this communication via the serial interface (RSKO protocol) for
Ecodrive and Diax. But you could also communicate with Indradrive. The DriveServer
is started. In the DriveServer, the interface used for the communication must be set.
In the debug window of the DriveServer, the communication over the serial interface
can be monitored and recorded. If a drive is to be addressed in an RS-485 bus, the
RS-485 operation must be activated in the DriveServer.
*** 6. Online RS232 Indradrive ***
This communication takes place via the serial interface via the
SIS protocol. For communication, the SCP and its DDE server are started.
All drives supporting the SIS protocol (Indradrive und Ecodrive) are addressed.
During the establishment of a connection, the attempt to establish the connection with
an existing configuration is always made. If the SCP does not contain any valid
configuration, the current connection settings are displayed and you then have the
possibility to establish a connection via "Scan drives".
*** 7. Online via SERCANS ***
During the establishment of a connection communication takes place via a SERCANS card
under the serial interface that was set, via the SCP and its DDE server. Therefor
the attempt is first made to use an existing configuration with SERCANS card in the
SCP. If the establishment of communication fails, a configuration is automatically
created in the SCP. If it is impossible to find a SERCANS card, the current connection
settings are displayed. If the dialog with the connection settings is closed with "ok",
the attempt to establish a connection is made immediately.
*** 8. Online via field bus ***
DriveTop is able to communicate via Profibus with drives of the Ecodrive range.
In this case the communication takes place via the Hilscher Communication Interface
PCMCIA PROFIBUS-DP/FMS master.
The precondition is a correctly configured Hilscher CIF-Device driver.
This type of communication, however, is only supported with field bus drive firmware
releases higher than FWA-ECODR3-FGP-03V24-MS and FWA-DRIVE*-FGP-20V12-MS.
If a valid parameter channel has been configured on the Hilscher Communication Interface
PCMCIA PROFIBUS-DP/FMS master, DriveTop will use this valid parameter channel.
But if there isn't any parameter channel valid, DriveTop will use a temporary parameter
channel for communication. The value of the parameter P-0-4083 "Length of parameter
channel in DP" is irrelevant in this case and can be zero.
*** 9. Simulation Offline ***
During a simulation offline, the DriveServer is started. It contains an offline
configurator, with which you can create projects. A project can comprise up to
127 different drives (Ecodrive, Diax). Afterwards, you can open existing projects
in DriveTop. During the offline configuration, you set all the hardware components
like amplifier, motor type, as well as the used firmware. The offline simulation
allows you to create parameter backups, which you can load again in an online
session.
*** 10. Causes for noise in communication on RS232/485 Ecodrive/Diax ***
To ensure an error-free communication the serial interface, the FIFO buffer
for the interface in use must be deactivated:
- Windows 95 and Windows 98:
With "Settings->Control Panel->System->Device Manager->;Ports",
open the properties dialogue of the serial interface in use for the
communication (COM1 - COM8). In "Port Settings->Advanced",
deactivate now the FIFO.
- Windows NT 4.0:
Deactivate the FIFO with
"Settings->Control Panel->;Ports->Settings->Advanced".
- Windows 2000:
Deactivate the FIFO in
"Settings->Control Panel->System->Hardware->Device Manager->;Ports->
Port Settings->Advanced".
SIEMENS PG:
***********
Some Siemens PG's use Power Management. In order for DriveTop to be able to
communicate without errors to the drives using the serial interface, you must
disable the Power Management in the BIOS for these Siemens PG's (APM disabled).
LAPTOP:
*******
In order to prevent errors in the serial communication, some laptops require
that the battery power monitoring is disabled in the BIOS.
*** 11. Malfunction in dialog "Motor parameters" ***
If it is not possible to select motor type keys in the dialog
"Drive functions->Motor parameters" under the tab "Indramat motor",
database access components may be not correctly installed.
Remedy: Start the program mac_typ2.exe in the subdirectory DriveTop\16V11\MDAC.
Then restart the DriveTop setup and select the option "repair".
*** 12. Field weakening operation of asynchronous motors with IndraDrive ***
In the case of IndraDrive, the voltage loop for field weakening operation of asynchronous
motors is set by motor-specific values of
- P-0-0553, Voltage loop proportional gain
- P-0-0534, Voltage loop integral action time.
For asynchronous Rexroth motors there aren't yet any motor-specific values available for
these parameters. It therefore is default values that are first taking effect for these
parameters. They have to be manually set to motor-specific values!
Calculating of motor-specific values:
P-0-0533 = 3.0 / [ P-0-4036 * P-0-0018 * (P-0-4039 + P-0-4040) ]
P-0-0534 = P-0-4043
Within a short time there will be manufacturer-side motor-specific values available!
They will be made available when loading the motor parameters via the "DriveTop" commissioning
tool or, if required, via the motor data memory.
*** 13. Error at program start of DriveTop ***
If an error message is generated at the program start of DriveTop, its cause might be MDAC - Microsoft Database
Access Components - not working correctly. Database access is controlled via MDAC.
Please install a current version of MDAC - Microsoft Database Access Components -
in the language matching your operating system, e.g. in version 2.8, English:
http://www.microsoft.com/downloa ... 396c&DisplayLang=de
When doing this, please observe the Microsoft safety instructions!
Then please reinstall DriveTop 16Vxx.
The DriveTop CD contains the English version of MDAC 2.5 (in subdirectory DatabaseComponents\MDAC).
*** 14. Error at start of oscilloscope function ***
If an exception occurrs at the start of the oscilloscope function, as a workaround delete the files
"osci.arv" and "osci.set" in subdirectory "System" of the current DriveTop version
(e.g. C:\Programs\Indramat\DriveTop\16V11\System).
*** 15. Crash when opening a file selector ***
DriveTop crashes on some US Windows 95 systems in the menu item "File->Open project"
and in the dialogs "File->Load", "File->Save" in the function "Change".
The cause is a incompatible system dll (comdlg32.dll).
This dll can be changed by executing the setup
"Comdlg Bugfix\setup.exe" on the DriveTop CD.
Attention: The replacement of the incompatible Dll version by the compatible Dll
belonging to this system could affect functions of other programs.
*** 16. Requried user rights (Windows 2000, XP with NTFS filesystem) ***
DriveTop requires write permission to the directories in which DriveTop was installed. For Windows 2000 with NTFS file system it is therefore necessary to provide this write permission for all users who need DriveTop.
DriveTop 16VRS reuires write permission to the
- DriveTop directory,
in standard installation: C:\program files\Indramat\DriveTop\...
- DriveTop driectory for the common files,
in standard installation: C:\program files\common files\IndShared\..
In windows operating systems with a NTFS filesystem all users working with DriveTop 16VRS must have this write permission.
With the command cacls in the command line the administrator could give the users or user groups the needed rights. Look also in the windows help about the cacls command.
Examples:
Rights for all members of the group: Assign user:
cacls "c:\program files\Indramat\DriveTop /t /e /g user:f
cacls "c:\program files\common files\IndShared\DriveTop" /t /e /g user:f
*** 17. Supported firmware online ***
- FWA-ECODRV-SSE-02VRS-MS
- FWA-ECODRV-SSE-03VRS-MS
- FWA-DIAX03-AHS-03VRS-MS
- FWA-DIAX03-ASE-02VRS-MS
- FWA-DIAX03-ATE-01VRS-MS
- FWA-DIAX03-ELS-04VRS-MS
- FWA-DIAX03-ELS-05VRS-MS
- FWA-DIAX03-SHS-02VRS-MS
- FWA-DIAX03-SHS-03VRS-MS
- FWA-DIAX03-SSE-01VRS-MS
- FWA-DIAX03-SSE-02VRS-MS
- FWA-DIAX03-SSE-03VRS-MS
- FWA-DIAX03-STE-01VRS-MS
- FWA-DIAX04-AHS-03VRS-MS
- FWA-DIAX04-ASE-02VRS-MS
- FWA-DIAX04-ATE-01VRS-MS
- FWA-DIAX04-ELS-05VRS-MS
- FWA-DIAX04-SHS-02VRS-MS
- FWA-DIAX04-SHS-03VRS-MS
- FWA-DIAX04-SSE-01VRS-MS
- FWA-DIAX04-SSE-02VRS-MS
- FWA-DIAX04-SSE-03VRS-MS
- FWA-DIAX04-STE-01VRS-MS
- FWA-ECODR3-FGP-01VRS-MS
- FWA-ECODR3-FGP-02VRS-MS
- FWA-ECODR3-FGP-03VRS-MS
- FWA-DRIVE*-FGP-20VRS-MS
- FWA-ECODR3-SGP-01VRS-MS
- FWA-ECODR3-SGP-03VRS-MS
- FWA-DRIVE*-SGP-20VRS-MS
- FWA-ECODR3-SMT-01VRS-MS
- FWA-ECODR3-SMT-02VRS-MS
- FWA-DRIVE*-SMT-20VRS-MS
- FWA-ECODR3-MGP-01VRS-MS
- FWA-INDRV*-MTH-01VRS-MS
- FWA-INDRV*-MPH-02VRS-MS
- FWA-INDRV*-MPB-02VRS-MS
- FWA-INDRV*-MPD-02VRS-MS
- FWA-INDRV*-MPH-03VRS-MS
- FWA-INDRV*-MPB-03VRS-MS
- FWA-INDRV*-MPD-03VRS-MS
- FWA-SERCAN-SER-02VRS-MS
- FWA-SERCAN-SER-03VRS-MS
- FWA-SERCAN-SER-04VRS-MS
- FWA-SERCAN-SER-05VRS-MS
*** 18. Online via field bus supported firmware ***
- FWA-ECODR3-FGP-03V24-MS and higher
- FWA-DRIVE*-FGP-20V12-MS and higher
*** 19. Supported firmware offline ***
- FWA-DIAX03-ASE-02VRS-MS
- FWA-DIAX03-AHS-03VRS-MS
- FWA-DIAX03-SHS-03VRS-MS
- FWA-DIAX03-SSE-03VRS-MS
- FWA-DIAX04-ASE-02VRS-MS
- FWA-DIAX04-AHS-03VRS-MS
- FWA-DIAX04-SHS-03VRS-MS
- FWA-DIAX04-SSE-03VRS-MS
- FWA-ECODR3-FGP-01VRS-MS
- FWA-ECODR3-FGP-02VRS-MS
- FWA-ECODR3-FGP-03VRS-MS
- FWA-ECODR3-FGP-20VRS-MS
- FWA-ECODR3-SGP-01VRS-MS
- FWA-ECODR3-SGP-03VRS-MS
- FWA-ECODR3-SGP-20VRS-MS
- FWA-ECODR3-SMT-01VRS-MS
- FWA-ECODR3-SMT-02VRS-MS
- FWA-ECODR3-SMT-20VRS-MS
【必讀】版權免責聲明
1、本主題所有言論和內容純屬會員個人意見,與本論壇立場無關。2、本站對所發內容真實性、客觀性、可用性不做任何保證也不負任何責任,網友之間僅出于學習目的進行交流。3、對提供的數字內容不擁有任何權利,其版權歸原著者擁有。請勿將該數字內容進行商業交易、轉載等行為,該內容只為學習所提供,使用后發生的一切問題與本站無關。 4、本網站不保證本站提供的下載資源的準確性、安全性和完整性;同時本網站也不承擔用戶因使用這些下載資源對自己和他人造成任何形式的損失或傷害。 5、本網站所有軟件和資料均為網友推薦收集整理而來,僅供學習用途使用,請務必下載后兩小時內刪除,禁止商用。6、如有侵犯你版權的,請及時聯系我們(電子郵箱1370723259@qq.com)指出,本站將立即改正。
|